Conductive Heat Transfer
Conduction as heat transfer takes place if there is a temperature gradient in a solid or stationary fluid medium.
With conduction energy transfers from more energetic to less energetic molecules when neighboring molecules collide. Heat flows in direction of decreasing temperatures since higher temperatures are associated with higher molecular energy.
Conductive heat transfer can be expressed with "Fourier's Law"
q = (k / s) A dT
= U A dT (1)
q = heat transfer (W, J/s, Btu/hr)
k = Thermal Conductivity of material (W/m K or W/moC, Btu/(hr oF ft2/ft))
s = material thickness (m, ft)
A = heat transfer area (m2, ft2)
U = k / s
= Coefficient of Heat Transfer (W/(m2K), Btu/(ft2 h oF)
dT = t1 - t2
= temperature gradient - difference - over the material (oC, oF)
Example - Conductive Heat Transfer
A plane wall is constructed of solid iron with thermal conductivity 70 W/moC. Thickness of the wall is 50 mm and surface length and width is 1 m by 1 m. The temperature is 150 oC on one side of the surface and 80 oC on the other.
The conductive heat transfer through the wall can be calculated
q = ((70 W/moC) / (0.05 m)) ((1 m) (1 m)) ((150 oC) - (80 oC))
= 98000 (W)
= 98 (kW)
Conductive Heat Transfer Calculator.
This calculator can be used to calculate conductive heat transfer through a wall. The calculator is generic and can be used for both metric and imperial units as long as the use of units is consistent.
Conductive Heat Transfer through a Plane Surface or Wall with Layers in Series
The heat conducted through a wall with layers in thermal contact can be calculated as
q = dT A / ((s1 / k1) + (s2 / k2) + ... + (sn / kn)) (2)
dT = t1 - t2
= temperature difference between inside and outside wall (oC, oF)
Note that heat resistance due to surface convection and radiation is not included in this equation. Convection and radiation in general have major impact on the overall heat transfer coefficients.
Example - Conductive Heat Transfer through a Furnace Wall
A furnace wall of 1 m2 consist of 1.2 cm thick stainless steel inner layer covered with 5 cm outside insulation layer of insulation board. The inside surface temperature of the steel is 800 K and the outside surface temperature of the insulation board is 350 K. The thermal conductivity of the stainless steel is 19 W/(m K) and the thermal conductivity of the insulation board is 0.7 W/(m K).
The conductive heat transport through the layered wall can be calculated as
q = ((800 K) - (350 K)) (1 m2) / (((0.012 m) / (19 W/(m K))) + ((0.05 m) / (0.7 W/(m K))))
= 6245 (W)
= 6.25 kW
Thermal Conductivity Units
- Btu/(h ft2 oF/ft)
- Btu/(h ft2 oF/in)
- Btu/(s ft2 oF/ft)
- Btu in)/(ft² h °F)
- MW/(m2 K/m)
- kW/(m2 K/m)
- W/(m2 K/m)
- W/(m2 K/cm)
- W/(cm2 oC/cm)
- W/(in2 oF/in)
- kJ/(h m2 K/m)
- J/(s m2 oC/m)
- kcal/(h m2 oC/m)
- cal/(s cm2 oC/cm)
- 1 W/(m K) = 1 W/(m oC) = 0.85984 kcal/(h m oC) = 0.5779 Btu/(ft h oF) = 0.048 Btu/(in h oF) = 6.935 (Btu in)/(ft² h °F)
• Heat Loss and Insulation
• Insulation
• Thermodynamics
• Thermodynamics
Online calculator, figures and table showing thermal conductivity of carbon dioxide, CO2, at temperatures ranging from -50 to 775 °C (-50 to 1400 °F) at atmospheric and higher pressure - Imperial and SI Units.
Cooling Mode - Heat Flux
Heat fluxes for various cooling or heat transfer modes.
Energy Transfer Equation
Fluid energy transfer.
Foods - Thermal Conductivities
Thermal conductivity of selected foodstuff like apples, beef, sugar and more.
Heat Exchangers - Fouling and Reduced Heat Transfer
Heat-transfer in heat exchangers are reduced by fouling.
Insulation Materials - Operating Temperature Limits
Temperature limits for commonly used insulation materials.
International Standard Atmosphere
International standard atmosphere in elevation -2000 to 30000 metre - pressure, temperature, density, viscosity, thermal conductivity and velocity of sound.
Online calculator, figures and table showing thermal conductivity of methane, CH4, at temperatures ranging from -160 to 725 °C (-260 to 1300 °F) at atmospheric and higher pressure - Imperial and SI Units.
Nitrogen - Thermal Diffusivity vs. Temperature and Pressure
Figures and tables showing thermal diffusivity of nitrogen at varying temperarure and pressure, SI and Imperial units.
Overall Heat Transfer Coefficient: Definitions, Values & Applications
Pipes and Cylinders - Conductive Heat Loss
Conductive heat losses through cylinder or pipe walls.
Thermal conductivity of plastics.
Steel Pipes - Heat Loss Diagram
Heat loss from steel pipes and tubes - dimensions 1/2 to 12 inches.
Thermal Conductivity of Common Materials - Solids, Liquids and Gases
Thermal conductivity of various common materials, including metals, gases, and building materials. Essential data for engineers, architects, and designers working with heat transfer and insulation.
Thermal Conductivity Units Converter
Thermal Transmittance vs. Thermal Resistance
The thermal transmittance U vs. the thermal resistance R.
Understanding Convective Heat Transfer: Coefficients, Formulas & Examples