Overall Heat Transfer Coefficient: Definitions, Values & Applications
Heat transfer through a surface like a wall can be calculated as
q = U A dT (1)
q = heat transfer (W (J/s), Btu/h)
U = overall heat transfer coefficient (W/(m2K), Btu/(ft2 h oF))
A = wall area (m2, ft2)
dT = (t1 - t2)
= temperature difference over wall (oC, oF)
The overall heat transfer coefficient for a multi-layered wall, pipe or heat exchanger - with fluid flow on each side of the wall - can be calculated as
1 / U A = 1 / hci Ai + Σ (sn / kn An) + 1 / hco Ao (2)
U = the overall heat transfer coefficient (W/(m2K), Btu/(ft2 h oF))
kn = thermal conductivity of material in layer n (W/(m K), Btu/(hr ft °F))
hc i,o = inside or outside wall individual fluid convection heat transfer coefficient (W/(m2K), Btu/(ft2 h oF))
sn = thickness of layer n (m, ft)
A plane wall with equal area in all layers - can be simplified to
1 / U = 1 / hci + Σ (sn / kn) + 1 / hco (3)
Thermal conductivity - k - for some typical materials (not that conductivity is a property that may vary with temperature)
- Polypropylene PP : 0.1 - 0.22 W/(m K)
- Stainless steel : 16 - 24 W/(m K)
- Aluminum : 205 - 250 W/(m K)
Convert between Metric and Imperial Units
- 1 W/(m K) = 0.5779 Btu/(ft h oF)
- 1 W/(m2K) = 0.85984 kcal/(h m2 oC) = 0.1761 Btu/(ft2 h oF)
The convection heat transfer coefficient - h - depends on
- type of fluid - if its gas or liquid
- flow properties like velocity
- other flow and temperature dependent properties
Convective heat transfer coefficient for some common fluids:
- Air - 10 to 100 W/m2K
- Water - 500 to 10 000 W/m2K
Multi-layered Walls - Heat Transfer Calculator
This calculator can be use to calculate the overall heat transfer coefficient and the heat transfer through a multi-layered wall. The calculator is generic and can be used for metric or imperial units as long as the use of units is consistent.
Heat Transfer Thermal Resistance
Heat transfer resistance can be expressed as
R = 1 / U (4)
R = heat transfer resistance (m2K/W, ft2 h°F/ Btu)
The wall is split in sections of thermal resistance where
- the heat transfer between the fluid and the wall is one resistance
- the wall it self is one resistance
- the transfer between the wall and the second fluid is a thermal resistance
Surface coatings or layers of "burned" product adds extra thermal resistance to the wall decreasing the overall heat transfer coefficient.
Some typical heat transfer resistances
- static layer of air, 40 mm (1.57 in) : R = 0.18 m2K/W
- inside heat transfer resistance, horizontal current : R = 0.13 m2K/W
- outside heat transfer resistance, horizontal current : R = 0.04 m2K/W
- inside heat transfer resistance, heat current from down upwards : R = 0.10 m2K/W
- outside heat transfer resistance, heat current from above downwards : R = 0.17 m2K/W
Example - Heat Transfer in Air to Air Heat Exchanger
An air to air plate exchanger with area 2 m2 and wall thickness 0.1 mm can be made in polypropylene PP, aluminum or stainless steel.
The heat transfer convection coefficient for air is 50 W/m2K. Inside temperature in the exchanger is 100 oC and outside temperature is 20 oC.
The overall heat transfer coefficient U per unit area can be calculated by modifying (3) to
U = 1 / (1 / hci + s / k + 1 / hco) (3b)
The overall heat transfer coefficient for heat exchanger in
- polypropylene with thermal conductivity 0.1 W/mK is
UPP = 1 / (1 / (50 W/m2K) + (0.1 mm) (10-3 m/mm) / (0.1 W/mK) + 1 / (50 W/m2K))
= 24.4 W /m2K
The heat transfer is
q = (24.4 W /m2K) (2 m2) ((100 oC) - (20 oC))
= 3904 W
= 3.9 kW
- stainless steel with thermal conductivity 16 W/mK:
USS = 1 / (1 / (50 W/m2K) + (0.1 mm) (10-3 m/mm) / (16 W/mK) + 1 / (50 W/m2K))
= 25 W /m2K
q = (25 W /m2K) (2 m2) ((100 oC) - (20 oC))
= 4000 W
= 4 kW
- aluminum with thermal conductivity 205 W/mK:
UAl = 1 / (1 / (50 W/m2K) + (0.1 mm) (10-3 m/mm) / (205 W/mK) + 1 / (50 W/m2K))
= 25 W /m2K
= 4000 W
= 4 kW
Typical Overall Heat-Transfer Coefficients
- Free Convection Gas - Free Convection Gas : U = 1 - 2 W/m2K (typical window, room to outside air through glass)
- Free Convection Gas - Forced liquid (flowing) water : U = 5 - 15 W/m2K (typical radiator central heating)
- Free Convection Gas - Condensing Vapor Water : U = 5 - 20 W/m2K (typical steam radiators)
- Forced Convection (flowing) Gas - Free Convection Gas : U = 3 - 10 W/m2K (superheaters)
- Forced Convection (flowing) Gas - Forced Convection Gas : U = 10 - 30 W/m2K (heat exchanger gases)
- Forced Convection (flowing) Gas - Forced liquid (flowing) water : U = 10 - 50 W/m2K (gas coolers)
- Forced Convection (flowing) Gas - Condensing Vapor Water : U = 10 - 50 W/m2K (air heaters)
- Liquid Free Convection - Forced Convection Gas : U = 10 - 50 W/m2K (gas boiler)
- Liquid Free Convection - Free Convection Liquid : U = 25 - 500 W/m2K (oil bath for heating)
- Liquid Free Convection - Forced Liquid flowing (Water) : U = 50 - 100 W/m2K (heating coil in vessel water, water without steering), 500 - 2000 W/m2K (heating coil in vessel water, water with steering)
- Liquid Free Convection - Condensing vapor water : U = 300 - 1000 W/m2K (steam jackets around vessels with stirrers, water), 150 - 500 W/m2K (other liquids)
- Forced liquid (flowing) water - Free Convection Gas : U = 10 - 40 W/m2K (combustion chamber + radiation)
- Forced liquid (flowing) water - Free Convection Liquid : U = 500 - 1500 W/m2K (cooling coil - stirred)
- Forced liquid (flowing) water - Forced liquid (flowing) water : U = 900 - 2500 W/m2K (heat exchanger water/water)
- Forced liquid (flowing) water - Condensing vapor water : U = 1000 - 4000 W/m2K (condensers steam water)
- Boiling liquid water - Free Convection Gas : U = 10 - 40 W/m2K (steam boiler + radiation)
- Boiling liquid water - Forced Liquid flowing (Water) : U = 300 - 1000 W/m2K (evaporation of refrigerators or brine coolers)
- Boiling liquid water - Condensing vapor water : U = 1500 - 6000 W/m2K (evaporators steam/water)
• Heat Loss and Insulation
• Insulation
• Insulation and Heat Loss from Steam and Condesate Pipe Lines
Heat loss from uninsulated and insulated steam and condensate pipes and tanks. Calculate insulation thicknesses.
• Thermodynamics
Conductive Heat Transfer
Convective Air Flow from Heat Source
Convective air flows from typical heat sources like people, computers, radiators and more.
Typical heat exchanger materials and their thermal conductivities.
Heat Exchangers - Fouling and Reduced Heat Transfer
Heat-transfer in heat exchangers are reduced by fouling.
Heat Exchangers - Overall Heat Transfer Coefficients
Overall heat transfer coefficients in common heat exchanger designs - tubular, plate or spiral.
Heat Transfer Coefficients in Heat Exchanger Surface Combinations
Radiation - Surface Emissivity Coefficients
Radiation emissivity of common materials like water, ice, snow, grass and more.
Radiation Heat Transfer
Submerged Coils - Heat Transfer Coefficients
Heat transfer coefficients for steam and hot water coils submerged in oil tanks.
Thermal Conductivity of Common Materials - Solids, Liquids and Gases
Thermal conductivity of various common materials, including metals, gases, and building materials. Essential data for engineers, architects, and designers working with heat transfer and insulation.
Thermal Transmittance vs. Thermal Resistance
The thermal transmittance U vs. the thermal resistance R.
Understanding Convective Heat Transfer: Coefficients, Formulas & Examples
Windows - Inside Condensation
Water condensation on inside glass windows surfaces vs. outside temperature and inside temperature and humidity.