Thermal Expansion of Steam Pipes - (inches)
Expansion of steam pipes when pressurized and heated from room temperature.
Operating Temperature (oF) | Expansion (inches per 100 ft Pipe) |
150 | 0.75 |
200 | 1.15 |
250 | 1.6 |
300 | 2.0 |
350 | 2.4 |
400 | 2.9 |
450 | 3.3 |
500 | 3.8 |
Note! - to avoid unacceptable stress and damage in a steam pipe line - handle expansion properly.
Example - Expansion of Steam Pipe
make 3D models with The Engineering ToolBox Sketchup Extension
A system is designed for pressure 120 psi with operating temperature 350 oF. As indicated in the table above (350 oF) the expansion is is approximately 2.4 in100ft pipe.
The expansion of a 90 ft long pipe can be calculated as
dl = ((2.4 in100ft) / (100 ft)) (90 ft)
= 2.2 in
• Sizing of Steam and Condensate Pipes
Dimensions of steam and condensate pipe lines. Calculate pressure losses, recommended velocities, capacities and more.
• Steam and Condensate
Calculate ring (or pipe) diameter expansion or contraction when temperature changes.
Linear Thermal Expansion Coefficients of Materials
Linear thermal expansion coefficients of common materials, including metals, plastics, and composites.
Linear Thermal Expansion: Formula, Coefficients & Calculator
Piping Materials - Temperature Heat Expansion and Cooling Contraction
Expansion and contraction when cast iron, carbon and carbon molybdenum steel, wrought iron, copper, brass and aluminum pipes are heated or cooled.
Sizing Steam Pipes (kg/h)
Steam is a compressible gas where pipe line mass flow capacity depends on steam pressure.
Sizing Steam Pipes (lb/h)
Steam Pipes - Sizing
Sizing of steam pipe lines - major and minor loss in steam distribution systems.
Steam Pipes - Thermal Expansion
Thermal expansion of steam pipes heated from room temperature to operation temperature (mm pr. 100 m pipe).
Steel Pipes Expansion Loops - Design and Calculation
Steel pipe expansion loops and their importance in managing thermal expansion, and how to design and size them effectively. Key considerations, calculations, and installation tips to prevent stress and damage in piping systems.