Latent Heat Flow
Latent Heat Flow - English (Imperial) units
The latent heat flow due to moisture in air can be expressed in English (Imperial) units as
Ql = 60 hwe ρ q Δx                                   (1)
Ql = latent heat flow (Btu/hr)
hwe = 1060 - latent heat of vaporization of water (Btu/lb)
ρ = 0.075 - air density at standard conditions (lb/ft3)
q = measured air flow (ft3/min)
Δx = difference in humidity ratio (lbh2o /lbdry_air )
Latent Heat Flow - SI-Units
The latent heat flow due to moisture in air can be expressed in SI-units (metric) as
Ql = hwe ρ q Δx / 3600                                  (2)
Ql = latent heat flow (kW)
hwe = latent heat of vaporization of water (2454 kJ/kg - in air at atmospheric pressure and 20 oC)
ρ = air density at standard conditions (1.202* kg/m3)
q = air flow (m3/hr)
Δx = difference in humidity ratio (kgh2o /kgdry_air)
*Note that properties of air changes with temperature. Interpolate values if necessary.
Example - Latent Heat Flow
A ventilation system transports 10000 m3/h of air through a building.
The state of the make-up (supply) air is 0 oC and 100% relative humidity. From the Mollier diagram the humidity ratio - x - can be estimated to 0.0037 (kgh2o /kgdry_air).
The state of the room air is 20 oC and 40% relative humidity. From the Mollier diagram the humidity ratio can be estimated to 0.0057 (kgh2o /kgdry_air).
The latent heat flow can be calculated as
Ql = (2465.56 kJ/kg) (1.202 kg/m3) (10000 m3/h) ((0.0057 (kgh2o /kgdry_air )) - (0.0037 ( kgh2o /kgdry_air ))) / 3600
= 16.5 kW
Air Psychrometrics
Air - Humidity Ratio
Air Heating Systems
Air heating buildings - heat supply vs. air flow and temperature.
Cooling and Heating Equations
Cooling Load - Latent and Sensible Heat
Latent and sensible cooling loads to consider when designing HVAC systems.
Great Sensible Heat Factor - GSHF
The Great Sensible Heat Factor is the ratio sensible to total heat in a cooling coil.
Heat Recovery Efficiency
Humid Air - Heating
Liquids - Latent Heat of Evaporation
Latent heat of vaporization for fluids like alcohol, ether, nitrogen, water and more.
Melting and Boiling Temperatures - Evaporation and Melting Heats common Materials
Melting and boiling point temperatures, latent heat of evaporation, and melting heat of common substances like copper, gold, lead and more - SI units.
Moist Air - Enthalpy
Propane - Latent Heat of Vaporization vs. Temperature
Latent heat with vaporized propane.
Removing Heat with Air
Calculating heat removed with air by measuring the wet bulb temperature.
Room Sensible Heat Factor - RSHF
Room Sensible Heat Factor - RSHF - is defined as the sensible heat load divided by the total heat load in a room
Sensible Heat Flow
Sensible heat is dry heat causing change in temperature but not in moisture content
Sensible Heat Ratio - SHR
The ratio Sensible Heat (or Cooling) Load to the Total Heat (or Cooling) Load.
Steam and Vapor Enthalpy
Vapor and steam enthalpy, specific enthalpy of saturated liquid, saturated vapor and superheated vapor.
Thermodynamic Properties of Saturated Steam: Data & Charts in Bar
Saturated Steam Table with properties like boiling point, specific volume, density, specific enthalpy, specific heat and latent heat of vaporization.