Liquid, Steam and Gas - Flow Factor Kv
By using flow factors the capacities of valves with different sizes, different types and from different manufacturers - can be compared.
The flow factor Kv is in general determined experimentally expressing
- flow capacity in metric units - m3/h - that a valve will pass for a pressure drop of 1 bar
Kv Liquids
Volumetric flow:
Kv = q (ρ / (1000 (pu - pd)))1/2 (1)
Kv = flow coefficient
q = volume flow (m3/h)
ρ = density (kg/m3)
pu = upstream pressure pressure (bar abs)
pd = downstream pressure pressure (bar abs)
Mass flow:
Kv = m / (1000 ρ (pu - pd))1/2 (1b)
m = mass flow (kg/h)
Example - Control Valve for Water and Kv Value
The Kv value for a valve with water flow 3000 kg/h and upstream pressure 10 bar and downstream pressure 7 bar can be calculated with (1b) as
Kv = (3000 kg/h) / (1000 (1000 kg/m3) ((10 bar) - (7 bar)))1/2
= 1.7
Kv Saturated Steam
pd > pu / 2:
Kv = 0.032 m (vd/ (pu - pd))1/2 (2)
pu = upstream pressure (bar abs)
pd = downstream pressure (bar abs)
vd = specific weight of downstream steam and actual temperature (m3/kg)
pd < pu / 2:
Kv = 0.032 m (2 vd2 / pu)1/2 (2b)
vd2 = specific volume for steam with pressure pu/ 2 and actual temperature (m3/kg)
Kv Gases
pd > pu/ 2:
Kv = 0.0019 q (ρg Tu / (pd (pu - pd)))1/2 (3)
q = volume flow of gas at 0 oC and 1013 mbar (m3/h)
ρg = density of gas at 0 oC and 1013 mbar (kg/m3)
Tu = upstream temperature (K)
pd < pu/ 2:
Kv = 0.0039 q (ρg Tu)1/2 / pu (3b)
• Control Valve Sizing
Butterfly Valves - Flow Coefficients Cv
Typical flow coefficients - Cv - for butterfly valves.
Control Valves for Water Flow – Kv Sizing & Pressure Drop Calculations
Control valve sizing and pressure drop calculations for water flow applications. Different valve types, Kv flow coefficients, and how to select the right valves.
Flow Coefficient Cv vs. Flow Factor Kv
Comparing flow coefficients Cv to flow factors Kv.
Valve Authority
The valve authority expresses the ratio between pressure drop across the control valve compared to total pressure drop across the whole system.
Water Control Valves - Flow Factor Kv Diagram