Exhaust Outlets - Capturing Air Velocities
The capturing air velocity in a distance x from an exhaust outlet can be calculated as
vc = q / (4 π x2)
= vo A / (12 x2)
= vo π d2 / (48 x2) (1)
q = air volume flow (m3/s, ft3/s)
A = duct area (m2, ft2)
vc = capture air velocity in distance x from exhaust outlet (m/s, ft/s)
vo = air velocity in the exhaust outlet opening (m/s, ft/s)
d = diameter of exhaust outlet (m, ft)
x = distance from exhaust outlet (m, ft)
Note! According to line one of the equation (1) - the capture velocity is not dependent on the size of duct. This equation can only be used for exhaust outlets with relatively small diameters.
For larger exhaust outlets equation (1) should be modified to
vc = vo A / (A + 10 x2)
= q / (A + 10 x2) (2)
Example - Capturing air velocity for a smaller exhaust outlet
Capturing air velocity in distance 250 mm from a 250 mm duct with internal air velocity of 3 m/s can be calculated as
vc = (3 m/s) π (0.250 m)2/ (48 (0.250 m)2)
= 0.2 m/s
Note! The air velocity in distance one diameter from the duct outlet - is less than 10% of the duct air velocity.
Exhaust Outlet Velocity Calculators
The velocity in distance x from an exhaust outlet can be calculated with the calculators below.
Smaller Outlets
Larger Outlets
- free apps for offline use on mobile devices
Exhaust Outlets in Walls or with Flanges
If the exhaust outlet is in a wall or with a flange the evacuation efficiency is improved and can be expressed as
vc = 1.33 vo A / (A + 10 x2)
= 1.33 q / (A + 10 x2) (3)
The calculator above can be used if volume is multiplied with 1.33. Use of exhaust hoods improves the evacuation efficiency further.
• Ventilation Systems
Duct Velocity
Calculate velocities in circular and rectangular ducts - imperial and SI-units - online calculator.
Evacuation of Air - minimum Capture Velocities to avoid Pollution products transferred to the Room
Capture velocities to avoid pollution products from galvanic baths, spray painting boxes and more contaminating the surrounding room and environment.
Exhaust Hoods
Sizing of exhaust hoods - air volume flow and capture velocities - online exhaust hood calculator.