Beam Fixed at One End and Supported at the Other - Single Point Load
Beam fixed at one end and supported at the other - single point load Bending Moment
MA = - F a b (L + b) / (2 L2)                               (1a)
MA = moment at the fixed end (Nm, lbf ft)
F = load (N, lbf)
MF = Rb b                               (1b)
MF = moment at point of load F (Nm, lbf ft)
Rb = support load at support B (N, lbf)
Deflection
δF = F a3 b2 (3 L + b) / (12 L3 E I)                                  (1c)
δF = deflection (m, ft)
E = Modulus of Elasticity (Pa (N/m2), N/mm2, psi)
I = Area Moment of Inertia (m4, mm4, in4)
Support Reactions
RA = F b (3 L2- b2) / (2 L3)                                 (1d)
RA = support force in A (N, lbf)
RB = F a2 (b + 2 L) / (2 L3)                                 (1f)
RB = support force in B  (N, lbf)
Beam Fixed at One End and Supported at the Other - Continuous Load
Beam fixed at one end and supported at the other - continous load Bending Moment
MA = - q L2 / 8                                    (2a)
q = continuous load (N/m, lbf/ft)
M1 = 9 q L2 / 128                                       (2b)
M1 = maximum moment at x = 0.625 L  (Nm, lbf ft)
Deflection
δmax = q L4 / (185 E I)                                  (2c)
δmax = max deflection at x = 0.579 L (m, ft)
δ1/2 = q L4 / (192 E I)                                  (2d)
δ1/2 = deflection at x = L / 2   (m, ft)
Support Reactions
RA = 5 q L / 8                            (2e)
RB = 3 q L / 8                            (2f)
Beam Fixed at One End and Supported at the Other - Continuous Declining Load
Beam fixed at one end and supported at the other - continous declining load Bending Moment
MA = - q L2 / 15                               (3a)
q = continuous declining load (N/m, lbf/ft)
M1 = q L2 / 33.6                              (3b)
M1 = maximum moment at x = 0.553 L (Nm, lbf ft)
Deflection
δmax = q L4 / (419 E I)                                  (3c)
δmax = max deflection at x = 0.553 L   (m, ft)
δ1/2 = q L4 / (427 E I)                                  (3d)
Support Reactions
RA = 2 q L / 5                            (3e)
RB = q L / 10                            (3f)
Beam Fixed at One End and Supported at the Other - Moment at Supported End
Beam fixed at one end and supported at the other - moment at the supported end Bending Moment
MA = -MB / 2                               (4a)
Deflection
δmax = MB L2 / (27 E I)                                  (4b)
δmax = max deflection at x = 2/3 L   (m, ft)
Support Reactions
RA = 3 MB / (2 L)                                 (4c)
RB = - 3 MB / (2 L)                                (4d)