Resistance vs. Resistivity
Electrical resistance and resistivity.
Electrical resistance of an electrical conductor depends on
  • the length of the conductor
  • the material of the conductor
  • the temperature of the material
  • the cross-sectional area of the conductor
Electrical resistance of a conductor can be calculated as
R = ρ L / A
   = L / (σ A)                                    (1)
R = resistance of the conductor (ohms, Ω)
ρ = resistivity of the conductor material (ohm metre, Ω m)
σ = electrical conductivity (1/ohms m, 1/Ω m, siemens/m, S/m, mho/m)
L = length of conductor (m)
A = cross-sectional area of conductor (m2)
Resistivity of some Common Conductors
  • Aluminum: 2.65×10-8 Ω m (0.0265 μΩ m)
  • Carbon: 10×10-8 Ω m (0.10 μΩ m)
  • Copper: 1.724×10-8 Ω m (0.0174 μΩ m)
  • Iron: 10×10-8 Ω m (0.1 μΩ m)
  • Silver: 1.6×10-8 Ω m (0.0265 μΩ m)
Note that resistivity depends on temperature . The values above are for temperatures 20 oC .
Resistivity of some Common Insulators
  • bakelite: 1×1012 Ω m
  • glass: 1×1010 - 1×1011 Ω m
  • marble: 1×108 Ω m
  • mica: 0.9 ×1013 Ω m
  • paraffin oil: 1×1016 Ω m
  • paraffin wax (pure) : 1×1016 Ω m
  • plexiglass: 1×1013 Ω m
  • polystyrene: 1×1014 Ω m
  • porcelain: 1×1012 Ω m
  • pressed amber: 1×1016 Ω m
  • vulcanite: 1×1014 Ω m
  • water, distilled: 1×1010 Ω m
Note that good conductors of electricity have low resistivity and good insulators have high resistivity.
Example - Resistance of a Conductor
The resistance of 10 meter gauge 17 copper wire with cross sectional area 1.04 mm2 can be calculated as
R = (1.7×10-8 Ω m) (10 m) / ((1.04 mm2)(10-6 m2/mm2))
= 0.16 Ω
Example - Cross-sectional area and Resistance
The copper wire above is reduced to gauge 24 and cross-sectional area 0.205 mm 2. The increase in resistance can be calculated to
R = (1.7×10-8 Ω m) (10 m) / ((0.205 mm2)(10-6 m2/mm2))
= 0.83 Ω
Convert between Electrical Resistivity Units
  • 1 Ω m = 0.001 kΩ m = 102 Ω cm = 39.37 Ω inch = 3.28 Ω foot
Resistivity Compared to Copper
  • Aluminum (pure): 1.6
  • Brass: 3.7-4.9
  • Cadmium: 4.4
  • Chromium: 1.8
  • Copper (hard-drawn): 1.03
  • Copper (annealed): 1.00
  • Gold: 1.4
  • iron (pure): 5.68
  • Lead: 12.8
  • Nickel: 5.1
  • Phosphor Bronze: 2.8-5.4
  • Silver: 0.94
  • Steel: 7.6-12.7
  • Tin: 6.7
  • Zinc: 3.4