Control Valves for Water Flow – Kv Sizing & Pressure Drop Calculations
Control valve sizing and pressure drop calculations for water flow applications. Different valve types, Kv flow coefficients, and how to select the right valves.
The table below can be used to estimate the Kv values for process control valves used in water systems.
- Go to the left column and select the pressure drop for the valve
- Go right in table close to the actual water flow. Interpolate to find the approximately Kv value
Pressure drop | Water flow (kg/h) | |||||||||||
36 | 72 | 108 | 144 | 180 | 360 | 720 | 1080 | 1440 | 1800 | 3600 | ||
(kPa) | (bar) | Water flow (kg/s) | ||||||||||
0.01 | 0.02 | 0.03 | 0.04 | 0.05 | 0.1 | 0.2 | 0.3 | 0.4 | 0.5 | 1 | ||
1 | 0.01 | 0.36 | 0.72 | 1.1 | 1.4 | 1.8 | 3.6 | 7.2 | 10.8 | 14.4 | 18.0 | 36.0 |
2 | 0.02 | 0.25 | 0.51 | 0.76 | 1.0 | 1.3 | 2.6 | 5.1 | 7.6 | 10.2 | 12.7 | 25.5 |
3 | 0.03 | 0.21 | 0.42 | 0.62 | 0.83 | 1.0 | 2.1 | 4.2 | 6.2 | 8.3 | 10.4 | 20.8 |
4 | 0.04 | 0.18 | 0.36 | 0.54 | 0.72 | 0.90 | 1.8 | 3.6 | 5.4 | 7.2 | 9.0 | 18.0 |
5 | 0.05 | 0.16 | 0.32 | 0.48 | 0.64 | 0.80 | 1.6 | 3.2 | 4.8 | 6.4 | 8.1 | 16.1 |
10 | 0.1 | 0.11 | 0.23 | 0.34 | 0.46 | 0.57 | 1.1 | 2.3 | 3.4 | 4.6 | 5.7 | 11.4 |
20 | 0.2 | 0.08 | 0.16 | 0.24 | 0.32 | 0.40 | 0.80 | 1.6 | 2.4 | 3.2 | 4.0 | 8.1 |
30 | 0.3 | 0.07 | 0.13 | 0.2 | 0.26 | 0.33 | 0.66 | 1.3 | 2.0 | 2.6 | 3.3 | 6.6 |
40 | 0.4 | 0.06 | 0.11 | 0.17 | 0.23 | 0.28 | 0.57 | 1.1 | 1.7 | 2.3 | 2.9 | 5.7 |
50 | 0.5 | 0.05 | 0.10 | 0.15 | 0.20 | 0.25 | 0.51 | 1.0 | 1.5 | 2.0 | 2.6 | 5.1 |
100 | 1 | 0.04 | 0.07 | 0.11 | 0.14 | 0.18 | 0.36 | 0.72 | 1.1 | 1.4 | 1.8 | 3.6 |
200 | 2 | 0.03 | 0.05 | 0.08 | 0.10 | 0.13 | 0.25 | 0.51 | 0.76 | 1.0 | 1.3 | 2.6 |
300 | 3 | 0.02 | 0.04 | 0.06 | 0.08 | 0.10 | 0.21 | 0.42 | 0.62 | 0.83 | 1.0 | 2.1 |
400 | 4 | 0.02 | 0.04 | 0.05 | 0.07 | 0.09 | 0.18 | 0.36 | 0.54 | 0.72 | 0.9 | 1.8 |
500 | 5 | 0.02 | 0.03 | 0.05 | 0.06 | 0.08 | 0.16 | 0.32 | 0.48 | 0.64 | 0.8 | 1.6 |
1000 | 10 | 0.01 | 0.02 | 0.03 | 0.05 | 0.06 | 0.11 | 0.23 | 0.34 | 0.46 | 0.57 | 1.1 |
2000 | 20 | 0.01 | 0.02 | 0.02 | 0.03 | 0.04 | 0.08 | 0.16 | 0.24 | 0.32 | 0.40 | 0.80 |
3000 | 30 | 0.01 | 0.01 | 0.02 | 0.03 | 0.03 | 0.07 | 0.13 | 0.20 | 0.26 | 0.33 | 0.66 |
4000 | 40 | 0.01 | 0.01 | 0.02 | 0.02 | 0.03 | 0.06 | 0.11 | 0.17 | 0.23 | 0.28 | 0.57 |
7200 | 10800 | 14400 | 18000 | 36000 | 72000 | 108000 | 144000 | 180000 | 360000 | 720000 | ||
2 | 3 | 4 | 5 | 10 | 20 | 30 | 40 | 50 | 100 | 200 | ||
1 | 0.01 | 72.0 | 108 | 144 | 180 | 360 | 720 | 1080 | 1440 | 1800 | 3600 | 7200 |
2 | 0.02 | 50.9 | 76.4 | 102 | 127 | 254 | 509 | 763 | 1019 | 1273 | 2546 | 5091 |
3 | 0.03 | 41.6 | 62.4 | 83.1 | 103 | 207 | 415 | 623 | 831 | 1039 | 2078 | 4157 |
4 | 0.04 | 36.0 | 54.0 | 72.0 | 90.0 | 180 | 360 | 540 | 720 | 900 | 1800 | 3600 |
5 | 0.05 | 32.2 | 48.3 | 64.4 | 80.5 | 161 | 321 | 483 | 644 | 805 | 1610 | 3220 |
10 | 0.1 | 22.8 | 34.2 | 45.5 | 56.9 | 113 | 227 | 342 | 455 | 569 | 1138 | 2277 |
20 | 0.2 | 16.1 | 24.2 | 32.2 | 40.3 | 80.5 | 161 | 242 | 322 | 402 | 805 | 1610 |
30 | 0.3 | 13.2 | 19.7 | 26.3 | 32.9 | 65.7 | 131 | 197 | 263 | 329 | 657 | 1315 |
40 | 0.4 | 11.4 | 17.1 | 22.8 | 28.5 | 56.9 | 114 | 171 | 228 | 285 | 569 | 1138 |
50 | 0.5 | 10.2 | 15.3 | 20.4 | 25.5 | 50.9 | 102 | 153 | 204 | 255 | 509 | 1018 |
100 | 1 | 7.2 | 10.8 | 14.4 | 18.0 | 36.0 | 72.0 | 108 | 144 | 180 | 360 | 720 |
200 | 2 | 5.1 | 7.6 | 10.2 | 12.7 | 25.5 | 50.9 | 76.4 | 102 | 127 | 255 | 509 |
300 | 3 | 4.2 | 6.2 | 8.3 | 10.4 | 20.8 | 41.6 | 62.4 | 83.1 | 104 | 208 | 416 |
400 | 4 | 3.6 | 5.4 | 7.2 | 9.0 | 18.0 | 36.0 | 54.0 | 72.0 | 90.0 | 180 | 360 |
500 | 5 | 3.2 | 4.8 | 6.4 | 8.1 | 16.1 | 32.2 | 48.3 | 64.4 | 80.5 | 161 | 322 |
1000 | 10 | 2.3 | 3.4 | 4.6 | 5.7 | 11.4 | 22.8 | 34.2 | 45.5 | 56.9 | 114 | 228 |
2000 | 20 | 1.6 | 2.4 | 3.2 | 4.0 | 8.1 | 16.1 | 24.2 | 32.2 | 40.3 | 80.5 | 161 |
3000 | 30 | 1.3 | 2.0 | 2.6 | 3.3 | 6.6 | 13.2 | 19.7 | 26.3 | 32.9 | 65.7 | 131 |
4000 | 40 | 1.1 | 1.7 | 2.3 | 2.9 | 5.7 | 11.4 | 17.1 | 22.8 | 28.5 | 56.9 | 114 |
Example - Kv for a Water Control Valve
For a water control valve with
- pressure drop 2 bar
- water flow 1 kg/s
- the Kv value should be approximately 2.6 according the table above.
Kv can be calculated as:
Kv = q / (dp)1/2 (1)
Kv = Kv value
q = water flow (m3/h)
dp = pressure drop (bar)
Related Searches
control valves • water flow • valve sizing • pressure drop • flow coefficient • Cv calculation • valve selection • fluid dynamics • hydraulic calculations •