Hot Water Expansion Tanks - Sizing
Required hot water expansion volume in open, closed and diaphragm tanks.
Expansion tanks are required in heating, cooling or air condition system to avoid unacceptable increases of system pressures when water expands during heat-up.
Explosive Power of Super-heated Water
  • 1 lb (0.45 kg) of nitroglycerin > 2 000 000 ft lbf (2 700 000 J)
  • 1 lb (0.45 kg) of water flashed into steam > 750 000 ft lbf (100 000 J)
Water - temperature rise and pressure rise in a closed system
Expansion tanks are in general designed as
  • open tanks
  • closed compression tanks
  • diaphragm tanks
Net expansion volume of water when heated can be expressed as
Vnet = (v1 / v0) - 1                                      (1)
Vnet = expansion volume of water (ft3, m3)
v0 = specific volume of water at initial (cold) temperature (ft3/lb, m3/kg)
v1 = specific volume of water at operating (hot) temperature (ft3/lb, m3/kg)
Open Expansion Tanks
Open expansion tanks
Required volume of an open expansion tank can be expressed as
Vet = k Vw ((v1 / v0) - 1)                                     (2)
Vet = required expansion tank volume (gallon, liter)
k = safety factor (approximately 2 is common)
Vw = water volume in the system (gallon, liter)
Note that in an open expansion tank fresh air is constantly absorbed in the water and tends to corrode the system. Open expansion tanks must also be located above the highest heating element, in general on the top of buildings, where they may be exposed to freezing.
Water - temperature volume expansion diagram
Closed Compression Expansion Tanks
Closed compression tanks can be designed as
  • adjustable expansion tanks - air is evacuated or injected by automatic valves to the tanks to control system pressures when temperature and expansion of water rises or falls
  • pump-pressured cushion tanks - water is evacuated or injected to the systems to compensate for temperature rise or fall
  • compression tanks with closed gas volumes - the tanks contains specific volumes of gas which is compressed when temperatures and system volumes increase
Water - Closed expansion tanks
Required volume in a closed expansion tank
Vet = k Vw ((v1 / v0) - 1) / (( pa / p0) - ( pa / p1))                                          (3)
pa = atmospheric pressure - 14.7 (psia)
p0 = system initial pressure - cold pressure (psia)
p1 = system operating pressure - hot pressure (psia)
Water - closed expansion tank sizing diagram
  • initial temperature 50 oF
  • initial pressure 10 psig
  • maximum operating pressure 30 psig
Diaphragm Expansion Tanks
Required volume in a diaphragm expansion tank
Vet = k Vw ((v1 / v0) - 1) / (1 - ( p0 / p1))                            (4)
Water - diaphragm exspansion tank sizing diagram
  • safety factor aprox. 2
  • acceptance factor aprox. 0.5
Example - Volume in Open Expansion Tank
A system with 1000 gallons of water is heated from 68 oF to 176 oF .
Minimum expansion volume in an open expansion tank with a safety factor 2 can be calculated as
Vet = 2 (1000 gallons) (((0.01651 ft3/lb) / (0.01605 ft3/lb)) - 1)
= 57 (gallons)
